SIEMENS SIPTROTEC RELAY 7SD5 COMMUNICATION TO MICROSCADA
Hi Am trying to integrate SIEMENS Siprotec 7SD5 relay to Microscada.I tried and configured siprotec relay SCD as mentioned in the document. But in CET the connection is getting toggling between "connection OK and Suepended". Please tell me the correct procedure to integrate the Siprotec to Microscada.
Thanks in advance
Answers
Check whether CET is reading RCB's or not. Second thing look for the client name under RCB and OPC server.
Usually it happens if file is different in relay and CET.
Usually it happens if file is different in relay and CET.
Make sure that the datasets configured in SIEMENS IED through Digsi is matching with the ones configured in CET.
Make sure also the RCB clients are configured properly in CET.
Make sure also the RCB clients are configured properly in CET.