I have a PM583 with PROFINET Master ,ACS355 with PROFINET adapter. i tried to control the drive . but in plc side, while scannig am not able to get a VFD as a slave device. Kindly suggest a right way to complete this communication.
Answers
Hi
You use Control Builder Plus or Automation Builder? The drive use Fena-01 or Fena-11 device?
Have you correct defined the IP adress in ACS355?
You must define menu as follow:
51.01 Ethernet
51.02 10 - PNIO DRIVE PROFILE
51.03 1 - 1= 100Mbps full duplex
51.04 0 - static IP
51.04 198 - first part of IP adress
51.06 168 - 2nd part of IP adress
51.07 20 - 3rd part of IP adress
51.08 10 - 4th part of IP adress
51.09 24 - subnet mask
51.10 198 - gateway adress
...
...
You need to follow the FENA instruction for Profinet use
PLC side
Make sure to have correct define the station name and the same IP adress that you have associate to drive.
Without other information, I could not give you more suggestions
Hope this help you