Display object description on Panel 800 for AC800M alarms
Our customer is working on a new project with 800xA, AC800M and Panel800. Alarms generated by AC800M are displayed on 800xA and Panel800 using MMS.
800xA can display object description found in the 800xA object linked to the alarm. But Panel800 does not display the object description because this information is not included in AC800M alarm messages. And I know object description is not included in OPC A&E specifications.
Is there any other way to display object description for AC800M alarms in Panel800?
Answers
Hello,
For sure, you can create your own Alarms in Panel Builder 800. Access Funcitions/Alarms (Ctrl+L) and clic in "Import", in the new window choose IO (begin and end is the same) and select "Alarm Group" where alarm will publish. When you import new alarm, will assign "retain" in "Alarm text" parameter by default. To change this, go to "Edit Multiple Language texts" in Setup/Multiple Languages/Edit, search "retain" value and assign as you need. Finally, check the change in Alarms.
Regards,
Cesar.