Problem with installation of RTA PU515A on 800xA Version 5.1
I'm installing a single node with AC400 connect. The PU515A is recognized in Device Manager as "Other PCI Bridge device" and "no driver found". When the 800xA installation comes to Advant AC400 connect I get an unknown error "0xe0000235" and installation stops, waiting OK to continue. This executable pu515DrvInstall.exe I tried a few times more, always getting the same error. The workstation used is an HP Z440 (3/2017) and the OS is Windows 7 with SP1 with the latest ABB approved updates.
I do not see any other HW conflict. The windows SI gives the problem as "drivers not installed". I cannot use any other slot to test, as it is the only one PCI available.
Can anybody advise how to solve this problem and if there are any steps to investigate the actual cause of problem e.g. if it is module HW error, computer HW incompatibility or SW incompatibility.
Regards
Voted best answer
I believe the PU515 driver does not work on 64-bit OS.
http://lmgtfy.com/?q=0xe0000235
64-bit kernel mode drivers need a level of cerification that is not met by ABB.
Suggest using PU410 instead. Downgrading to 32-bit Windows does not sound like a good idea.
by SavasSoultanidis Rank: 1337 on 3/21/2017 4:31:13 AM | Like (0) | Report
Hi Stefan, thanks for the answer. I searched more after your reply for the 64bit version of windows. You are correct. The answer was found in the manual "3BUA000156-511_F_en_System_800xA_5.1_Post_Installation" in page 109. I shall order a PU410 now. Regards,
Add new comment