PM865- Control Builder Safe HART CommunicationIn
In one of our terminal Autaomation project we have connected level transmitter of E&H male to our AI880 -HI Module.
Apllication is a SIL3 Application.
The O/P of E&H Radar level transmitter is 4-20mA and is configured in our program. According to the 4-20mA variation and scaling done in AI880 channel the level of tranmitter is coming. There is vary huge variation in the reading but actually the reading in the Radar Level transmiiter are not changing so frequently. This is due to 4-20mA signal variation and high level range of the storage Tank.
The E&H radar level trasmiiter is a HART device and can provide value on HART protocol.
Can we get the level values through HART in control builder safe and further it can be used for our logic in SIL3 level application
Is there any way to do this.
Answers
No,
And thats not what HART is for.
If your level measurement is noisy or isn't accurate you have a transmitter installation problem. FIX THE REAL PROBLEM.
Add new comment