How Generate Digital Output from PP-825 and get input in AC 800 Controller Application
I am using 800xA DCS system. The controllers are AC800Hi and software is Controller Builder Professional. I also used PP-825 connected directly to controller. I want to generate out put from PP-825 and get as input to controller for local operation as pump start/stop, Start-up- Override from PP-825. Please how to program PP-825 side & controller side.
Answers
OK, so you mean a Process Panel.. PP-825
Well, it depends what library objects you are using to control your motor connected to the pump, but most of the standard motor and valve objects have a "Panel" mode. You can connect Access Variables to the "Panel" connections for the motor object. The Process Panel can read/write to the Access variables using MMS
If you are using some other library or writing your own motor objects, then you should look at the standard process objects library to see how Panel mode works.
by admin Rank: 46 on 3/9/2014 7:55:08 PM | Like (0) | Report
In original post PP-825 was written as TP-825, it's corrected now and additional comments are deleted.
Cheers
-Admin