SMAR DC302 Configuration issue
We are facing the issue with SMAR DC302 Configuration with
VendorName = "SMAR"
ModelName = "DC302"
Revision= "08.5"
VersionOD =0x01
But Shows the version match while assigning the device.
OdIndex(TB0 DDItemId ox201EA) Value In Device (880), Value Capabilit (1240).
OdIndex(FB3 DDItemId ox2023A) Value In Device (1000), Value Capabilit (1360)
OdIndex(FB4 DDItemId ox20444) Value In Device (1120), Value Capabilit (1480).
We are not getting the proper DD files to Assign to the device.
Could anyone support on this.
Regards-
msmkacharya
Answers
You should request an object type at ABB Device Integration Center. This is the recommended solution.
If you have downloaded DD+CFF from Smar, there should be a CFF file version without predefined blocks, but with instantiable blocks. That one should work and the required blocks should be created and located during device assignment.
Alternatively you can patch the CFF file with the values found in the device. This will not work if there are more devices of this type with different block configuration and could be a dead-end, leading to trouble in the future.
Both methods are discouraged. Please contact Device Integration center.
Best regards
Jürgen