800xA how to change trend template for BMI AIS control module
Like in the topic. The problem is when I try to do it normal way by Config View of aspect Trend Display in Object type structure the possibility of choosing new trend template is disabled like in the attached picture.
Voted best answer
Hello,
If the library is released,then you are not allowed to change the Trend Template config view.
Please take the authorization from library owner before open the library for the change.
(It creates another version when you open and release it. Please be carfeful!)
Answers
Hi BP
You are right and it need to locked before release otherwise i afriad that we will lost the control on the standard libraries.
Why you want to change the standard DMI trend template (If you don't mind please share your idea)
In our system we have got mainly AC450 in PLC layer and for the analog signals from Advant we have got our standard template... I would like to use the same or similar template for signals from AC800M. This is request from operators to have it the same...
BMI library is protected but you can customize with the help of library Manager.
Contact your local ABB office to get a support from library manager.
Add new comment