Mapping list for REF 542 PLUS
ABB UNIGEAR MV switchgear with REF 542 plus for each cubicle is connected to engineering station through ethernet switch
i need the MODBUS mapping list for REF 542 plus , to be used at SCADA specially volt,power , current status signals
Answers
I think you can read the Modbus mappings from REF542plus with the Modbus Suite tool. This tool should come with the REF542plus Configuration Tool.
You can find information about the Modbus Suite in the later part of the Modbus Technical Reference manual: https://search-ext.abb.com/library/Download.aspx?DocumentID=1MRS755868&Lang
uageCode=en&DocumentPartId=&Action=Launch