I need to connect the PP877 to AC700 because I will make demo and config. that system for show to new customer in next week.I try to connect via TCP/IP .please help me for make that demo . I have to use Control Builder 2013 for 2 week and use Panel Builder 800 V.6 for 2 day. It will be good if teach me step by step.
Arthit,
I need to connect the PP877 to AC700 because I will make demo and config. that system for show to new customer in next week.I try to connect via TCP/IP .please help me for make that demo . I have to use Control Builder 2013 for 2 week and use Panel Builder 800 V.6 for 2 day. It will be good if teach me step by step.
Arthit,
Voted best answer
Hi,
I give you a few guidelines:
First Step: AC 700F should be slave on MODBUS TCP (configure in the HW structure of Control Builder F.
Second Step: Map the Variables that you need to be displayed on the Panel 800 using the MODBUS Function Blocks (Write Coil for Boolean and Write Register for Analog Signals), you may need to convert some datatypes
Third Step: in Panel Builder, use Controller MODICON / MODBUS TCP
Answers
Hello Arthit,
As commited find here with video on how to connect panel800 to freelance controller AC 900F. it's a same procedure for AC 700F. Check associated app.
by Sumit Gargav
Will share this via App this week. In case of urgent need get in contact with local abb sales colleague.
- Sumit