In my esd controller one channel variable declared wrongly .I need to change that variable but I couldn't ..
Answers
Hi,
You can click on the setting button in this page and change the Normal task to a lower or higher number, first test the lower number for example :5 ,then see the error, if the error remains again, set another number against 5,Adjust and test (until the error is not shown)
I didnt this procedure in Hi Integrity CPUs, so please be carefull to prevent unexpected shutdown.
BR
The issue is with Task configuration. Controller may get download in next attempt without any changes to TASK Configuration but in order to resolve this issue permanently, we can use Task Analysis tool for further configuration of TASK in offline or online mode.
Hello,
Picture clearly tells the tasks: normal and slow are colliding each other so use the offset to for both the task by diff of 10ms and 20ms to ensure there is no starting collisions