OPC Triconex
Hi,
I try to connect to OPC Triconex via 800XA OPCDA Connector service but i often have status "Initialize" then "Underfined" never in "Service" status
This OPC server is a Triconex OPC AE and DA Embedded Server ! I configured DCOM as mentionned on this website
http://support.softwaretoolbox.com/ap...
nsiderations-with-triconex-opc-ae-and-da-embedded-server
So now there is no error dcom.
After the dcom setting, the refresh button worked well so I can select the opc server id.
My question is: why the status is never on "Service" when opc connector try to connect this opc server ?
Anyone has the same problem ? What's is wrong in my setting ?
Thanks.
Answers
Even if DCOM lets you make the first basic connection to the server, it does NOT mean that everything is OK with DCOM ...
https://advosol.com/p-22-opc-security...
Work thorugh the security analyzer and fix any issues you may find
You also appear to have two service groups connected to Triconix. If these groups are supposed to be redundant then they are not properly configured - You should have one service group with two service providers.
If these service groups are all connected to the same OPC server, then check you have not exceeded the maximum allowed clients on the server.
Hi,
Thank a lot for your anwser. The first service group is made by my collegue when I was asked for this problem.
When I began to look for the failed connection, I created entire an generic OPC Network in Control Structure and the second service as you saw in picture.
The first one is disabled.
I have one OPC connection to Trioconex Opc server.
Thanks