We need to change version of AC800F to V2013 but the scada stay in conductor NT v9.1. We are trying to communicate by an gateway but when we load the gwy we had a message "Loading is not possible, DMS version is not compatible".
Answers
Hello JMSK,
The "DMS version is not compatible" error generaly means that the version of firmware/software is not compatible with version of Freelance Engineering/CBF. Have You reinstalled the gateway to a compatible version after updating Freelance?
Hope this helps,
Mike
Hello MMM,
Thx for your answer. I need to tell you more explications about our system.
We've got 2 stations : One with windows 7 and freelance 2013 (for CBF) and the other one with windows XP and ConductorNT V9.1 for the system scada.
Before, the CBF was on the same station of conductorNT in version 9.1.
Now, it's necessary for us to migrate the AC800F in 2013 version. For that case, we have separated into 2 stations but the communication between AC800F and conductorNT was broken.
In the project, the station conductorNT is declared to an UNI-GATEWAY.
How can we do with our system to communicate with conductorNT 9.1 and AC800F in 2013 version?
Dear JMSK,
I'm afraid that in this case I can't really help You much more. I did some digging and found out that:
(a) Conductor NT is discontinued and the last version was 6.0 (there was no v9.1, so maybe You though of Freelance 9.1)
(b) Last version of Conductor was compatible with Freelance 9.2, but I can't find any compatibility tests since 2010.
(c) Conductor NT v6.0 is in the Limited life cycle phase since 2013, so I assume they didn't develope/test any new features for it in regard to new Freelance versions.
You may try to install Conductor NTs Freelance AddOn component on Win7 machine, but I'm afraid there is simply no way to connect them this way. Maybe you should establish a different connection? OPC?
Best Regards,
Mike