Is it possible to do range convertion is 800xA History Log Configuration.
Hi,
I am reading some analog signals as percentage (1-100 %), but i need this to be converted to Level of range (0-500 meter) without changing it in the controller side and want to have History log and trend for meter range (0-500).
Thanks.
Voted best answer
With a Property Translation aspect you can easily perform a conversion, then log the converted property.
Add a Property Extension Info aspect to expose presentation attributes (min, max, no of decimals and engineering unit) to the trend.
/Stefan
Answers
Hello,
we have been using this by "Property Translation aspect". That is the easiest way out.
If dont want to use that then you can change/multiply your real input value(X) with 5 i.e.5X and move into a softvariable and then you can fetch trend of the soft variable rather than physical IO.But this is a messy process..I would suggest you to go with the first one.
Pl read "Appendix A" of the link provided. It is detailed explaination of the Aspect
Regards
Source: http://www05.abb.com/global/scot/scot...file/3BSE030322-510_A_en_System_800xA_Operations_5.1_Operator_Workplace_Configu
ration.pdf
by Invert Rank: 1623 on 2/15/2014 6:17:55 AM | Like (0) | Report
Also
I = input x 5
Output = i
Function block output for a new aspect you could use for logging and trends...