800xA system , Is it allowed to have same IP range for two different system
In 800xA system 5.0 /5.1, is it allowed to have same IP ranges for two different system and also can we have one common domain controller for two system in the same network?
Pls clarify..
Voted best answer
Hello,
Yes it is allowed to have same IP ranges for two Different systems (not the same IP)
Yes you can have one common domain controller for two systems, there are routing options.
BUT it is NOT advised to have this in the same network.
If you are requiring to place the two systems in the same network for purposes of multi system integration, you can divide(partition) the network into 'areas' for the different systems.
Best Regards
Add new comment