Failed to create ASO for aspect 'Hardware Status and Tag Navigation.
Dear All,
I am getting following error while adding any DI AI AO or DO module in Control Builder under given below path.
Hardware AC800M --> PM866/TP830 --> Modulebus.
Screenshot is also attached for reference.
Voted best answer
Check whether the Software and system extension for "AC 800M Status monitoring" is loaded in all the nodes of the system. Hope this could solve your problem.
Answers
Typically this kind of error means that you have included an Extension in the 800xA system, but forgotten to install that extension on the engineering station where you are creating the IO module.
I would guess the message comes from AC800M Status reporting.