In 800xA 5.1, how we can release a DO command if any new alarm/unacknowledged alarm in a particualr list.
Hi All,
In 800xA 5.1, how we can release a DO command if any new alarm/unacknowledged alarm exist in a particualr list.
Hope it can be done with Property Transfer definition but i dont know how to extract that property in the expression used in Property Transfer definition .
Thanks.
Voted best answer
Hello,
It can be done through Alarm Global Properties.
Use "IsUnAck" parameter, If "IsUnAck>0,then release DO command
Answers
The External Alarm service can also be be used to write boolean value depending on a specifical alarm lists's alarm state.
Hello,
For any such configuration, we generally use external alarm configuration available in 800XA. There you can define DO in the alarm column and to acknowledge it, you can also map a DI or soft signal.
You will need to setup a service for the same.
Regards