RTA board was working okay in the begining. Later, the Upload was not success and found the RTA status and Service are not okay. (Services are in "Initialize" status).
attached the screnshots.
And, tried the following steps,
1. Created new Network and Added the RTA board - problem is same.
2. Created New System and added the RTA board - problem is same.
Answers
OK, since you have no AC400 tags uploaded I'm guessing this is a new project ?
Is the board connected to a properly terminated MB300 Network ? Have you got another running node (eg controller, Advant OS) on that network ?
> "RTA board was working okay in the begining".
- Define carefully what you mean by "working".
Did the 800xA Services that use the RTA board all run and show status green ?
Did you see the RTA board alive on the system status page of other nodes in the system?
Did you get event messages from other nodes to indicate the board was running properly ?
Did you sucessfully connect to the RTA board with On-Line Builder ?
Did you load config files to it sucessfully ?
What did you change (before you made a new Network and 800xA System) that could have broken the board configuration ?
If you changed the Server, did you load the correct driver ?
Have you got a spare PU410 ?
Rob's right.
Do you get any System Messages in RTA Board Configuration (OnLine Builder) tool of the connectivity server? Please report them in full detail (in ASCII text, not images please).
The services will remain in Initialize state until at least one neighbour node is seen on the control network. Check your network settings.
Add new comment