Does Load changed objet will initialize the ressource after time zone change?
The ressource must be initialize after Time zone change.
Does Load changed objet will initialize the ressource after time zone change or we need to do load whole station?
Answers
Hello,
Yes, timezone change need whole station download and will stop controller for a while. or even change load object will stop controller and that is acknowledged to user via hint message.
CBF is very intutive, while changing timezone in configuration, hint message appears that user must initialise all resource, do you want to apply the changes ? if select yes.
Need to perform plausibility check > Save and download resource under CONF node which appear in red color bubble.(red color indicates there is impact on resource, controller/resource needs to be stop while download)
Note: after changing time zone successfully, recomended to set system time once in comissioning mode so that time master(controller) will take current time and follower will synch with, incase timesynchronisation is enabled on freelance network.
Hope that helps