CBF Version 6.2 VS Digitool
Dear Sir,
We have downgraded our CPU from Version 9.05 to 6.2 using CBF version 6.2 But our system version is freelance 2000 with configure by digitool v 6.1 freelance 2000.
The error which we got from system is unknown flash type. And after downloading OS is got disconnected. Should we downgrade CPU to version 6.1? Or any other solution is available.
We appreciate your prompt action.
Thanks.
Voted best answer
All the software and firmware versions in the whole Freelance system must be the same. It means that if You have a CPU with firmware version 6.2, the Operator Station must also have digivis version 6.2 etc.
You can eighter downgrade the whole system to version 6.1 or upgrade it to version 6.2 - whichever suits You better.
Answers
Dear Reza,please contact me at tomasz.sinczak@ae.abb.com or +971 50 818 65 45 and we can talk about your case with 6.1 and 6.2 Freelance controller Best RegardsTomasz
Source:
Add new comment