in DigiVis Alarms Prio 2 not readable. How can I Change color of letters for Prio 2
Freelance 9.2 Operators have Problems to read Alarms Prio 2 in color white letters on yellow. How can I change the color of letters for Prio 2.
Voted best answer
Here is what You can find in the documentation:
As You can see there is a way to change message display colors, but according to my knowledge it requires changes in DigiVis libraries. Please contact Your local ABB service to get some help with it.
Source: Engineering Manual - Operator Station Configuration
Answers
Hi,
As of now you can not change the color of "Alarm" or color of "Letter" for any Priority alarms in Freelance System, but you can change the Alarm Severity for only OPC Alarm (means you can change the priority of alarms) which is coming via OPC Server.
Add new comment