800xA for Freelance OPC Server.
Good day;
I have a system with a two Freelance Connectivity Servers. The OPCDA service is in initialize state in both server provider and the event collector service is in synchronizing also in both server provider and I think that these services have to be in Service state or Do we need to be connected to the controllers to get the status state in service?
In both Connectivity server the Freelance OPC server is running and the version is Freelance 2013. The 800xA System is 5.1 FP4 rev D.
Thanks in advance
Voted best answer
Hi Carlos,
As we discussed you need to connect conroller and download at least once to see OPC & AE services in "Service" status.
I hope this solves your quesry.:-)
Answers
Hello,
There are two things:
- Freelance OPC Server is running on the connectivity and is loaded from CBF?
- also the controller is loaded from CBF and connected so is possible to get data for the opc connection.
Hello,
In Freelance OPC Configure tool window, the connectivity servers of CS1 and CS2 resource ID configure as below example.
CS1->resource ID-58,alias ID-88.
CS2->Resource Id-59,alias Id-88.
The 800xA of service Structure setting,
Ex:OPC1,service group(Special Configuration window mention the Adapter identity that
"ABB.AdvDsOPCServeradapter.1").
Below the Service group Add Service provider -->CS1(58),CS2(59).
After Both the CS status get service, configure the Alarm collector(AE).
I hope it will work.