I need to control ABB Drives via Modbus TCP (AC800M). Does ABB have any tested library for this?
I have done some logics for this but they are not fully tested and I am not confident at all with them.
In another hand, for me is quite surprising that it seems that no libraries for controlling drives (with their standard profidrive sequence) via Profibus or Modbus are available.
Answers
For controlling drives by ProfiBus there are several libraries. Besides all specific libraries for pulp&paper, minerals, metals and so on, you have ProcessObjDriveLib which I beleive is contained within the standard package.
I bet that some unit within ABB also has a solution for ModBus communication. Check with your local representative.
Hello,
Try REUSE Library...I believe it has a standard function block by the name SBE_VSD which is specifically designed for drives interfacing with 800XA.
Regards
Add new comment