CI840 issue
Hi,
In one of the profibu slave, CI840 PRIM LED is switching between Primary and Secondary CI840 card. Also under Unit Status tab - Extended Status - I get the following error
"Parameter data fault, Redundant Slave does not exist, Redudant - What could be the issue? Other slaves (clusters) are working fine. Only this cluster CI840 and associated AO cards are not working.
Please let me know what could be the probable causes.
Answers
Hello,
Check the firmware is same in both ci840 you can check via hyperterminal.
Ensure both should be ci840A instead one may be ci840 and other may be ci840A.
If above are true then check the profibus connection is OK in both A and B lines ensure no crossover.