Changing AC700 IP address to 10.x.x.x network
Has any one had this issue previously and recieved some responses but have recently tried it again with no luck.
I have can see everything while the Controller boots up in terminal emulator and I see the place where it sais to push <space> to configure but it doesn't work. I have tried pushing <space> all the way through the boot process. I have tested my terminal emulator with other devices and the emulator accepts my commands.
I have the controller in stop mode I also removed the ETH cable incase that was part of the issue.
Please help
Voted best answer
Hi,
I checked with AC700F controller in 9.2 version, it is possible to change the IP address through hyperterminal, please have a look on attached controller log file for details.
First i have set ip as 172.16.1.7 subnet as 255.255.240.0 then i have changed to 10.140.42.20 subnet as 255.255.255.0.
Again i have changed to 10.140.42.58 and subnet as 255.255.255.0
Answers
Hi,
In AC700 you can change IP address using the front panel keys as an alternate method. Refer M&I manual for more information.
Hi,
You can change/Set the AC700 IP address in two methods which i mentioned below,
Method 1:
In this you can set/change only fourth octet of IP address, for eg: 172.16.1.x, only "x" can be changed
1. Reboot AC700F controller and press "CFG" button available on controller during reboot
2. Display will show IP Address, press ok
3. Set IP address using up and down arrow button, press ok
4. Display will show IP address and select save using up and down arrow button
5. Display will show "Start", press ok
Method 2:
Through Hyper terminal which you are following.
TK 501 Cable drawing I think this wiring should work cant find TK701 drawing
Hey Guys I figured out that the issue was the cable.
It turns out that the wiring for the TK501 is the same as the TK701 so attached is the TK501 cable wiring diagram.
Thanks for the help!
by Sumit Gargav
I wonder why there is an issue! I suggest get in contact with local ABB support line. If they can help via remote connectivity. It's interesting to know what is issue there ?
by MMM
Could You please give some more info: which system version are You using and is it first time You set the IP adress of this unit or do You only need change it?