Freelance DigiVis - Trends, operational log
HI
First Point
I have configured trends in operator station in Freelance 2013 SP1. when we are exporting the trends to excel we are getting all the data(6 variables) in trend blocks in single column. What is the way that I can get the data of each variable in separate column in excel.
Second Point
Similarly when I am exporting the data from opl to excel through digi browse (or even in digi browse also all the data configured are coming in single row
how is this possible to make the data in different rows as it appears in preview while configuriing.
Third point
how many operator log I can configure in Freelance in common pool.
Answers
Dear Himanshu
for your first topic you need to use the textimport function of Excel. Open an empty sheet and go to the data tab in the "Get external Data" group select "from Text". A wizard will open and allow you to split the text by the seperator ( semicolon or a comma) into different columns.
You can also directly open the file and use the "Text to Columns" function in the data tab in the Data Tools group.
For your second point I need to see the configuration, the preview and the view in DigiBrowse.
The answer to your 3rd. question is that each operator station can have 4 of each type of logs.
If you only put the logs in the common display pool then the answer is 4. If you already have 2 logs below an operator station resource, then the answer would be 2 for the Common Display Pool.
If you want more OPL logs, you should use the Excel Reports function of Freelance.
Add new comment