CI868 CSWI status Connection failed with this LN
Hi all,
i configured some IEC61850 MMS Configuration to the CI868 from REF630 IEDs, and all the LN's are ok with exception of the CSWI which is configured with Pos (ST) and has also the Pos_CTLCMD Out Port connected for sending Control Commands to the IED. However i only get Error Status for the whole LN (containing also Pos_stVal and Pos_stSeld Connections).
All Report Control Blocks configured are reporting enabled, and Data for all other LN's is received without Error.
Is there some additional Data for the CSWI that needs to be added to the RCB or some other settings that could give this behaviour?
Answers
Thanks for your answer.
I configured CSWI.Pos... attached the ICD for the REF630, whole SCD is something like 200MB. The CI868 is called TESTJ1T1 and i configured 2 RCB, one for the Analog Values and one for CSWI Pos (fc=ST).
Hi Backdraft,
I am working on a project with PCM600 2.5, 800xA 5.1 FP4 and REF615. I experienced the same issue today and instantly checked your SCD file for the Pos_stVal to see if it was read via MMS and GOOSE at the same time. Besides, I experienced an instability like once the GOOSE signal was available and MMS was not, and after another download the MMS was available but GOOSE was lost.
Anyway, it seems that we can pick only one method for a signal (I picked the MMS one), which is fair enough I think.
Quote from your comment:
"I think i found the issue, it looks like it is not supported to send the Position via GOOSE and MMS. Anyone to confirm this?
Now as i require the Position via GOOSE, it looks like MMS Commands can not be used..."
Add new comment