in 800Xa version 5.1 FP2 how to configure CI853 as a slave in modbus RTU configuration.
in 800Xa version 5.1 FP2 how to configure CI853 as a slave in modbus RTU configuration.
Normally we configure as a master any possible is the to configure as a slve in modbus configuration.
Answers
Hello,
Starting from 6.0.3 Ci853 supports as modbus RTU slave.
There is a modbus slave application example on this website. Note that modbus slave is not "officially" supported until version 6 - the example uses serialLib and works on older versions of xA
I would recommend to use Modbus Slave-Slave converter between the systems if other system can not be changed to slave. AC500 controller should be easy to program to work as Modbus Slave-Slave converter.