rnrp AC800M not visible
Voted best answer
Almost all looks good to me.
The firewall in Microsoft Windows may prevent RNRP from receiving the multicast traffic RNRP is dependent on. Try turning off the firewall and check if RNRP detect the controller.
The following raises some concern that the controller has issue with CN1 Ethernet, but you are able to ping, download and connect OPC server???
Try to get this error away (cold start, new cable, etc)
Answers
Here the results of our testing:
Test with other PC and other controller:
Wireshark
Hi Stefan,
it took me 2 days with new instalation of system and investigation. No results.
At last I changed a parameter at the NIC, I remembered on trouble with an other system with loop detection without loops, and it works. :-)
The parameter is:
Now the next and hopefully the last challenge is to set the time in controller.
It's a challenge because I have a combined system with AC800M Connect and AC400 Connect with RTA Board.
But these challange has to wait until next year.
Happy New year to you and your family.
Michael
The pictures are not visible :-(
Hi Stefan,
now we have solved all problems.
rnrp works, the controller communicates with each other and it is synchronized via SNTP.
Thanks a lot for your support.
Michael