How to modify existing faceplate in 800 xa ,pdf need
Answers
The object faceplat is located in object type str. for each object type.its recommended to you build your own faceplat with your requests and don not edit standard facepalt .by this way you will not have problem in upgrading your library.
if you want to edit exisiting faceplat,you can edit faceplat (body size,buttom location ,etc) and its attached aspect in object type str. for each object.
RTFM
3BSE049230: System 800xA Engineering - Process Graphics, Section 7 Faceplate Framework.
The instructions in this manual are for building your own faceplates for your own libraries.
DO NOT MODIFY Faceplates in standard ABB libraries unless you fully understand the consequences. Upgrades can become very difficult and all changes can be lost entirely when the system is upgraded to a new version. Extension Libraries must be used to preserve any modifications you may make to standard library faceplates.