RNRP Error (RNRP Wizard Utility)
Dear. Everyone
I have the error in RNRP Wizard Utility.
It's the error about Secondary Plant Network.
The plant network configuration is Aspect Servers(3ea), Connectivity Servers(4ea), Client(10ea), Engineering Station(2ea), HUB(4ea).
And this servers and clients network are divided by two HUB Hardwares.
1st HUB Connection : Aspect Servers(3ea), Connectivity Servers(2ea)
2nd HUB Connection : Connectivity Servers(2ea), Client(10ea), Engineering Station(2ea)
This two HUBs are connected by one LAN Cable.
Attached the picture.
If you see this error or know how to solve it, please let me know and reply the answer.
Thanks,
BR,
Answers
Error messages can be due to network overload (RNRP not able to send traffic) on secondary network. E.g. a network loop.
RNRP's Loop Detection is not bullet proof - the loop must be affecting RNRP's traffic for RNRP to detect loop. If packets of other kind (other multicast, e.g. NetBIOS, etc.) is looping, RNRP will not detect it.
The image indicate that you have redundant network, primary + secondary. How did you wire the two networks if you only have one set of hubs with uplink connection between?
The secondary network must be given its own set of switches/cables/hubs. If no such equipment exist for the moment you better disconnect all secondary cables and run with singular network until you have obtained hardware to host the secondary network on.
| PC1|PC2|PC3|...|
============== primary network
*** no connection between primary & secondary hardwares ***
============== secondary network
|PC1|PC2|PC3|...|
Add new comment