Periodic error message "Failed to collect 8 logs via collector OPC" SV4.1 with IM
Voted best answer
The message originate in Basic History and is most often due to a log is trying to log a no longer existing OPC item,
Starting with version 5, the Long Message contain the first five erroneous logs - so you can start the identification work immediately from the Details... window.
In earlier versions you must use AppLog to find out which logs have problems.
a) Login as a user member of the IndustrialITAdmin group in Windows domain/workgroup
b) Start->Run... afwapplogviewer
c) Click OK, accepting defaults in the two following dialog boxes
d) Select the node and Basic History (AdvHtHistorySrv) service provider emitting the error
e) Select Operations
f) Find & select the AdvHtHistorySrv(collection apartment operations) ListCollectorMap operation
g) Click Invoke
Below is a sample output - at the end are the "Pending logs" listed.
Pending = log is not collecting and result in the system event you have noticed.
Collector OPC (Data is collected through OPC2.0 DA interface.)
=====================================================================
progId=ABB.AdvHtOpcCollector.1
status=S_ADV_HT_COLLECTOR_OPERATE_NORMAL
isInitialized=true
cookies=10
pendingLogs=1
Cookies
=======
cookie 1: template=1m365d item=Program2:Program property=Temp1.Value logId={1E30DC66-DEE1-462F-9190-C9329D4391DF}
...
cookie 9: ...
Pending logs
=======
cookie 10: template=500ms_1week item=LogReal2:Function Block property=Value logId={BFD787F1-231E-4B9C-8BA1-67EF16680FEF}
The "item=" points to the object having the Log Configuration. Look it up with the Find Tool; then figure out if the log is obsolete, or can be repaired (select new valid OPC property, etc.).