Freelance 2000 CPU spare part
Hello,
Is it possible to get somewhere one CPU DCP 10 F 6.05.0 for spare part.
Thnks a lot for your help.
Pablo Ibáñez
Voted best answer
Please contact your local ABB Service contact.
For what reason do you need that exact hardware version, or did you mean a hatdware not below 6.05.0 ?
Answers
Hello,
CPU`s DCP 10 are still available as new, exchange and refurbished. Please contact :
parts-repair-control@de.abb.com
6.05.0 is only information about production:
4- Heiligenhaus FF
05 - month May
0- year 2000
For ordering is HW and SW Version necessary.
Regards
Rudolf Cypek
For what it is worth, the actual part number to order the DCP 10 Controller Module is: 0338701M, this part number replaces the older part number: 37211-0338701 in case this was the number that you were used to seeing.
This item is also available to purchase as Refurbished/Exchange as well as being repaired if you have a failed unit.
For pricing and availability, you should either contact your local ABB office that sells controls or the local ABB Control Products Distributor in your area for pricing.
Good luck.