800xA: "default view" for faceplates: unable to change faceplate settings in the "AdvantMasterObjectTypes" library
I want the "default view" size for all faceplates in my system to be "faceplate" instead of "reduced", but I'm unable to change this setting for faceplates in the AdvantMasterObjectTypes library.
Is this possible somehow? (Preferrably without copying the faceplates and making my own)
I attached some screenshots.
Answers
Hello,
if a library is "open" then you should be able to modify aspects.
I think your user has wrong settings.
Is your user synchronized with Windows, and is it included in OperateITUser/Admin ?
Local admin ?
Very often we have this kind of problem when users restore a copy from site and will work at the office with a copy.
/Ronny
I made the 800xAService user a member of "Software Developers". Now the "Default view" faceplate setting is no longer grey, but when I try to change it, I get the following error:
"Operation failed to execute! [Error] Changes on 'MB300 AI:Faceplate' are not allowed. Library 'AdvantMasterObjectTypesPG2Ext 1.2-0' is not open".
See the attached screenshot.
But as you can tell from the screenshot in my original question, the library is open!
(I'm well aware that adding a user to the "Software Developers" group is not recommended. I'm doing this on a test installation of 800xA only.)
Add new comment