800xa with AC400 connect and thirdparty interface
HI,
we have system configuration with 800XA 6.0 with AC450 system,
now we need to interface thirdparty PC for level-2 data exchange ( read & write)
kindly suggest the reliable configuration
regards
suresh s
Voted best answer
I have spent many many hours answering on similar questions here on AKS.
Please search AKS before asking!
http://lmgtfy.com/?q=abb+aks+1+3+9+seconds
http://lmgtfy.com/?q=abb+aks+mb300+anper
Please revert if you have any problems following the links above.
Answers
The attached slide show that there exist many ways for an OPC client to communicate with an OPC server.
For 800xA for Advant Master, the "Asynchronous Advise" and "Synchronous ReadFromCache" are the by far the most recommended methods in combination with active groups and items with 1, 3 or 9 seconds update rate.
- Download and read the Advant Master Configuration User's Guide, 3BSE030340-600.
- Download and read the Advant Master Performance Guideline, 3BSE042621
- Only subscribe to properties listed as cyclically subscribable in the Advant Master Configuration User's Guide.
- Only write to objects of MB300 DAT type, and as little as absolutely possible.
- Keep a close watch on ANPER task and channel analyze results on the RTA board and controllers.
- Do not overshoot 40-50% CPU load on RTA.
Add new comment