HART Devices not connecting
I have a 800xA 5.1 FP4 RevD RU2 with Tool Routing enabled in all controllers, AI815/AO815 connected via Optical Modulebus with the right position in "Property Management" and OPC-FBB-Data Source and Configuration in the project object running on AC800M CS servers.
When a try to connect to DTM, both generic HART and specific, it keeps connecting and never goes any further than that.
I observed that there is no OPC property for the devices in "Control Connections" so, I believe there is something wrong with that.
"FBB-OPC Configuration" aspect under tab "OPC Server Statistcs" shows 0 Hart Devices but I have them unde the correct channels in Control Structure.
Tips?
Answers
First of all there is no link between OPC control connection and FBB OPC Configuration with HART device not working. So take that out of equation.
Second use Fieldbus Management aspect, go online and make an upload of HART device. Does the upload end successful?
Paste the screen shot of result here if you get any error message.