TCP/IP Primary and Secondary Network indication in PCS HMI
Hi All,
The plant have two way of netwrok TCP/IP primary and secondary(wireless) network for the CSN(Client Server Network) and CN(Control Network). sometime the primary network down due to some reason and secondary network takes the control. there was no indication that the system works in secondary network right now, unless we open the network manager application of hirschmann to check the network status. we are using Hirschmann network equipments(switch, wireless and other)
1. How can show indication in 800xA that currently this controller network works with primary or secondary line?
Answers
When configured properly, RNRP and the System Status service will inject "Network Connection" alarms into the System Alarm and Event lists.
Try having a look there - pull a cable and expect an alarm with same content as the RNRP Monitor provides.
Greetings,
Also you can use PC, Network and System Monitoring Asset for monitoring Network status as an Asset Monitoring.
Please see below link for details: