800xA alarm hiding mask configuration
Hello, I would like to hide several alarms based on a boolean status tag. My invoking variable and analog tags are all in our 800F Freelance system. These tags and variables have been brought in to xA via the PLE import AC800F uploader. Based on equipment run status (bool) I would like to hide several analog alarms (low flow, high O2, low pressure etc.) First of all can I do this? If so can someone help with the hiding mask and hiding rules configuration please. Thank you very much.
Voted best answer
Yes
Create new Hiding Mask object in Library Structure
Add Hiding Rule aspect(s) on alarm owning objects
Configure some or all alarm conditions that shall be hidden on rule aspect for each object. Select Mask to govern Rule.
Both Mask and Rule allow activation via OPC DA property (both must be TRUE to activate hiding)
Regular hiding can not hide retroactively - this may be added to version 6 at some future time.
More information in users guides