Freelance - not working profibus CI801
Hi! I've got problem with establishing connection for CI801 via profibus. System is Freelance 8.2.6320. I've added everything for proper connection - similar to working one on site, but still I'm recieving "Parameter error on slave". When I use the same cable to connect with CI830 is everything working correctly - without making any changes in configuration.
Voted best answer
GSD - in 8.2 I've got empty DTM list. Problem is sloved - after installing Control Builder F it has got beta librarys connected instead a regular.
Answers
Hi.
I must ask what do You mean by "without making any changes in configuration". If You set up communikation for CI801 EXACLY the same as for CI830, You used wrong gds/dtm file... This can result in "Parameter error on slave" massage. In this case You must define the connection again, from the start, using proper gds/dtm file.
If that's not it - please describe the state of LEDs on CI801 and PROFIBUS Master.
by Sumit Gargav
Using DTM or GSD to configure slave ?