how can i upload a advant AC410 program?
Hi engineers
we have a emergency problem and we are going to upload AC410 program and back up that. how can i upload a advant master AC410 program and back up it ?
Is it possible? If answer is yes please help me and guide how we should do?
Answers
Dump source code with commands DUDBS and DUPCS. This code is readable.
It might be useful to have a full backup also, create one with command DUAP. This type of backup is not readable, but it can be restored rather quickly.
Please download the AMPL Application Building Reference Manual from ABB Library, 3BSE002417R601. A download account is probably required. Please speak to your regional ABB sales representative about gaining access.
Chapter 7 cover backup and restore of application
if you have a latest backup available. You can load that backup to the controller via online builder from an Enginnering station using LOAP Command
#LOAP FILENAME
Once the application is loaded you can backup using DUAP command
Add new comment