How to assign REM 615 current channels to the inputs of the MAPGAP blocks
According to client requirements we must implement a signal based on a current criteria, additionally to the high and low alarms and warnings that are defined.
We tried to assign the current channels to the inputs of the MAPGAP blocks but we haven’t been able to find a way to do that, neither in the configuration or in the signal matrix.
Please send us instructions on how to configure the MAPGAP inputs with phase current inputs.
We are using the following relays: ABB REM 615-H-B-M-B-CA-AH-N-B-A-8-A-N-N-2-1G
Answers
Measurement functions in 615 series devices has own alarm points. For example in CMMXU function settings you can select 4 different alarms which then can be used the IED application or sent with communication.
So no need to use MAPGAPC just for alarm limits.
by kstoilov
What is MAPGAP? Which connection are you establish between REM615 and MAPGAP?
Add new comment