Communication between Panel 800 and Controller AC800M
Hi, i'm Fadzrul Azim.
I want to ask question about communication between Panel 800 and Controller AC800M.
Firstly, how to change IP Address for Panel 800? the default ip is 192.168.1.1 and i want to change it to 172.16.4.XXX.
For transfer the file (graphic layout) to the Panel 800, what is the best way to transfer it? Using TCP/IP or Serial Cable? if serial cable, which Baudrate that i can use?
I already read the user manual and i still cannot solve the problem above.
Thanks!
Voted best answer
When you start the panel (connect power), you get a set-up menu. From here you can change the network setting (ip address).
The best way (by far) is to communicate via TCP/IP. Fastest and simplest.
Answers
Gtreetings
the communication between the Panel 800 and the AC800M is done using the TCP/IP
also you can configure it using the same protocol
To change the IP address you need to use the defualt on for the fist connection
but yoy can change it to any other IP address fro the panel configuration software
kindly notes the setting of the rear dip switches
Good luck
by fadzrul Rank: 3773 on 1/22/2014 8:24:36 PM | Like (0) | Report
thanks guys!
by admin Rank: 44 on 1/22/2014 9:28:31 PM | Like (0) | Report
Pls help in closing a question, by voting to an appropriate/correct answer.
-Admin