how to rights to change values i,e limits in pid in operating station
sir
we are using acs 800m controller builder 4.1.0 version we have eng , operating station but we require to change in limits of pid in operating station but we are change in engineering station ,
pl explain and changing procesure
Answers
1. Identify what permission that is required to write to the property if the PID
-> Use Control Module / Function Block - Property List -> write permission
2. Identify what permission operator has on PID object
-> Use operator account and process graphics, right click the PID object -> Details -> Permission
-> Optionally, click the permisson "missing" then click Explain to see why deny is in place
3. Create a Security Report
-> from the Domain Object in the Admin Structure, call the Security Report, click Update
With 1+2+3, decide whether operator account should be a) given permission, or b) if its better to lower the required permission.
a) is made with Security Definition aspect(s) - it also possible to change the default security aspect located on the Domain Object (where the Security Report resides)
b) is made with Property Attribute Override aspect(s). They work on type level and instance level, also on protected libraries. An open library can be changed from Control Builder M, Object Type -> Permissions.
All keywords are described in various user's guide - please search and read them!
Add new comment