Control Module position in CMD editor when doging a copy operation
Hi,
I'm having a single control module where I've instanciated some objects/tags.
Then I want to copy some of these to another single control module, SCM.
This can be done in the Engineering Workplace with copy and paste, one by one.
Then the object is inserted in the destination SCM at same POSITION and with same SIZE. This is what I'm after.
I want to do this with the Bulk Data Manager, BDM, but then the size of the inserted objects are equal to the size of the destination SCM, and the position is the center of the SCM!
Is it possible to use BDM to copy object from one SCM to another, and have them inserted in the same POSITION and with the same SIZE?
How to do it?
Yes, I know it's possible to copy the whole SCM in the Engineering Workplace :-)
Thanks in advance!
BR Rolf
Answers
This question has not yet been answered.
by rolflien Rank: 145 on 10/7/2016 2:18:14 AM | Like (0) | Report
Found one solution in BDM:
1. Drag in the Control Structure aspect
2. Drag in the source objects to BDM
3. Create the destination single control module if not existing
4. Rename the string/path of the Control Structure.ParentObject to the destination control module
5. Copy the content of the Object Identification column to the Source Object column (this is then pointing to the source object to be copied)
6. In the Object Identification column, rename to destination path
7. Add the Command Place in the columne
8. Press the Save All Object button