CP400 SOFT Uhandled Exception
I have just uploaded an aplication from CP450 T, I got the .AA6 and the .AF6 files, but when I try to reconstruct source I get a window with the message
"Unhanled Exception"
Out o f memory!
Ok to resume?
Yes No
If I choose No CP400 shuts down, if choose Yes, CP400 goes back to the last instruction
I have tried several times uploading the application with a different name but the result is the same.
I'm using CP400 Soft 1.4.0 (build 195)
Windows 10 Pro 64 bits
Any suggestion?
Answers
You can't edit directly .AA6 file, first you need to RECONSTRUCT it to .V6F file first.
From the manual:
Reconstruct Source is used to reconstruct an uploaded application file from *.AA6
to *.V6F. The application will be displayed on a PC and the source file (*.V6F) can
be saved for the future editing and application.
In CP400Soft, an application downloaded to an operator terminal can be rebuilt; Reconstruct Source enables you to directly reconstruct a source file of an uploaded application on an operator terminal from *.AA6 to *.V6F
Note:
This function is not available for all operator terminal models: please refer to Appendix
A - CP400Soft Features and Operator Terminal Models for complete details
Steps to reconstruct a source file from *.AA6 to *V6F:
1. On the operator terminal, select Upload Application. In CP400Soft, select File/
Upload Application. The operator terminal will upload the application to the PC and the file will be saved as *.AF6.
2. Next, select File/Reconstruct Source and open the application file (*.C64 or
*.AA6). The application appears on the PC and you can save the source file as *.V6F.
Add new comment