CI867 communicate with Mgate
Dear Parthiban T,
I have some problem about CI867 & MGate MB3180
I cannot communicate with slave via Mgate
I try to test by connect CI867 to Modbus Sim. Slave TCP the result is good
but when I try to connect Modbus Sim.via Mgate (Sim Slave Serial) the result is not working
Could you please recommend how to config MGate or Do you have any trick
Voted best answer
Hi again!
There is a traffic monitor function in the MGate Manager SW that can be useful!
See screen dump attached.
BR
Answers
Hi,
Please check the Control Builder configuration against the snapshot attached.
If the Modbus MGATE Device’s
IP is “192.168.50.56”
Serial Slave ID “1” - which is connected to MGATE,
Then Gateway IP should be “192.168.50.56”
Modbus Serial Slave Position should be "1" in the CEX Bus under the Gateway.
Hi!
A question about the physical layer; do you have correct status (LED) indication on the Moxa MGate?
(I've worked with MB3170, which has a number of indicators)
BR
Dear All,
Many thank for good anser.Now I try to do follow you and it is working.
Regards
Arthit