Data access write operation did not complete with in required time.
Our project is 800xa for advant master and 800xa for safegaurd and we have 2 aspect&connectivity server coonected to MB300 with RTA unit(PU410) and 6 client.
we can't do any action on one of objects and when we click on push bottum we faced this massege on operator massege list :
"Failed to write on property 'MORD_03' with permission 'Tune':Data access write operation did not complete with in required time".
this object type is "MB300 Group" and its connect to safegaurd node.
this object reset the addressable pannel for smoke detector that connected to safegaurd node by RS232.
thank you in advance
Answers
Please connect OnLine Builder and check for system messages in CPU(s) of SafeGuard controller and PU410(s) of operator.
Likely, there will be a system message somewhere.
With safeguard you need to setup the dual handling properly.
Please file case with service desk in Oslo in case you need professional support for SafeGuard.