800xA version 6 error
800xA version 6 error -As anyone seen this error.
800xa Version 6.02 update.
Voted best answer
Hi,
I had a similiar issue when upgrading to 6.0.1 RU2. Check to see if the MMS service is still shoing in the system services for that node. The issue i found was that the service was removed. Once i repaired the installation of the MMS product the MMS service reappeared and the OPC service was able to be restarted. Re Deploy was then performed and all worked ok.
Answers
The screenshot doesnt show much information except that one post install action for AC800M Connect has failed. Navigate to the log files to see which specific post install action failed. Then you can decide to either manualy resolve or fix the issue.
Attach the log file if you are not sure.