AI880A channel error with Status Code 16#120010
I am using PM865 ESD system for Fire & Gas System. i have configured one Gas detectors on Analog Input signal in channel # 3 and 4. both of these channels are in inhibited mode to normalize system. From CB i found status codes of both channel error wit error code 16#120010.
Please guide how to resolve this issue.
Answers
Hi,
16#120010 status reveal that :
16#1xxxxx: you have error in backup unit
16#x2xxxx: General warning
16#xxxx10: Channel error
So, please check your channel status whether it is not having open wire connection or the loop is maintained corrcetly with voltage/current.
As per attached Channel Status picture, I connected Normal signal wiring with faulty signal. Still faulty channel in error. I need support if this is a wiring issue or something else that i am missing.
Looking forward kind support to resolve this problem.
Kind Regards,
Nouman Shabbir