Im triying to simulate with softcontroller but appears this error. Error 9159: Controller:HW Build version for controller is not supported by Control Builder or differs between dependent controllers. How I can simulate the control builder application?
Voted best answer
As per our experience, this error comes only when there is an issue between available Library version of the Controller Vs the suuitbale Hardware Library connected in Hardware structure.
Answers
Hello,
Kindly check the hardware simulation is true in the path:tools-setup-station-application download-hardware simulation allowed
and make the controller node enable for the simulation.
An ensure if you are using in single node machine connect the node to any switch/laptop to detect/recognise mms to work properly while downloading to softcontroller.
ControlBuilder version and Soft build version may be different. Pls attach the Control Panel Screen shot for verfying the build information and also attach the Controlbuilder screen shot of error.
Hi
I faced the same problem.
my system is V5.1 FP4 Rev E
however the soft controller installed was 5.1
then i installed soft controller of V5.1 Rev E
I could download
Hope it helps you